Results 101 to 150 of 596
Hybrid View
-
22-04-2009, 05:39 PM #1
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Im too i search the catallogue ; informations for reefer tec
thanks monir_khatibi@hotmail.com
-
22-04-2009, 10:45 PM #2
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
tanks my tetsher i have one probleme for daikin end i want solution for this probleme
f 803 END F1O9 END F 107
I WAIT YOU SOON
-
06-04-2010, 03:32 AM #3
-
23-04-2009, 12:00 PM #4
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hallo
i bought the thermo king refrigerator container type hd-ha-ab951 2007 year. But i need manual.maybe you could help me!!!
-
24-04-2009, 08:05 PM #5
-
11-11-2009, 09:02 AM #6
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hello sr, I HAVE A PROBLEM WITH MY REFEER , HAS THIS MESSAGE. ENGINE STALLED. IDONT NOT WATH IS THAT CAN YOU HELP ME IM SORRY FOR MY BAD WRITER THANX SO MUCH
-
07-05-2009, 06:45 PM #7
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hi guys i am new here so pls excuse me but i am intrested in buying a small 3 tonne hino truck with an older thermoking md-1 Fuelsaver the hours shown are 2202 hrs . do you guys know anything about the reliability and dependability of these tks and would you pls let me know what i got to look for as this is my first truck and i want it to last a while
-
08-05-2009, 11:33 AM #8
-
09-05-2009, 05:52 PM #9
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
...................................
Last edited by reefermechanic; 27-02-2013 at 08:52 AM.
-
04-05-2016, 04:55 PM #10
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hello there. A question please.
SB 200 TG Reefer unit. I want to replace the filter dryer on this thing. Do I need to do a pump down at compressor service valves only?
Thank you in advance.
-
15-05-2009, 02:57 AM #11
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
I have a carrier Phoenix Advantage that I recently purchased. It's on a wreck that laid on it's side. It starts and runs good, blows cold, but the out of range light stays on and the numbers on the display keep counting down continuously, and I can't set temp. Any help would be greatly appreciated.
Thanks, Art
-
15-05-2009, 03:14 AM #12
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
I have a carrier Phoenix Advantage that I recently purchased. It's on a wreck that laid on it's side. It starts and runs good, blows cold, but the out of range light stays on and the numbers on the display keep counting down continuously, and I can't set temp. Any help would be greatly appreciated.
Thanks, Art
-
16-05-2009, 03:49 PM #13
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hey art
you need trailer guys for that problem...this is the container reefer side of the industry...plus units dont usually run very well on their sides. may sound like alot of problems
-
11-02-2016, 01:01 PM #14
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
its most likely a micro problem,a place in cali will go thru it for ya at a very reasonable price,here is their #7074250108
-
10-06-2009, 05:15 AM #15
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi PRO Reefer Mechanic,
I have problem with download data of daikin reefer machine, LXE-10D, have you send for me software DCCS new version. thank. email: pacificocean.info@gmail.com
-
10-06-2009, 06:31 AM #16
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi reefermechanic,
I have some problem with download data of reefer machine carrier and daikin, can you send for me software? thank
pacificocean.info@gmail.com
-
13-06-2009, 10:10 AM #17
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi all,
I am new in this business and i feel lost right now, can someone give me carrier and tk software and connection cable specification ???
Thank You !!!
-
17-06-2009, 08:58 AM #18
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi senior mec
Need the manuals for Daikin (all models) and Thermoking (smart reefers) Service Manuals.
Regards
-
13-07-2009, 02:41 PM #19
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hallo to all...
I'm new at this comunity and i'm so happy to have found you. I have a problem with a refeer container. Its an older one (1989) build by Graaff Germany, and it has Carrier Transicold machinery.
The problem is: it starts cooling fin until it reaches -3ºC. At that temp. it just turns off completely. Even the display turns off. It will eventually turn back on by it self after 15 min... How can i fix that..?
Do you have the instructions manual for that one?
Please help...
model nº.: 69NT40-394-9
Regards
Alex
-
13-07-2009, 05:00 PM #20
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi OttiliPY.
I donn t see like this model since a few years..Its very old but i think its working still
First you have to check to the "board,timing and current control".Usually somethings may burning on this card.I hope you will find problem..
Good luck
Reefer Mechanic.
-
14-07-2009, 12:12 PM #21
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
-
29-09-2009, 09:42 PM #22
-
14-07-2009, 12:02 AM #23
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hey man isee u are so genirus in dis forum so iwant ducement about thermoking instalations and dats my email didou_wind@yahoo.fr
thank's man
-
14-07-2009, 06:35 AM #24
-
16-07-2009, 10:03 PM #25
-
16-07-2009, 10:05 PM #26
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
tanks may tetsher i have probleme in refeer daikin al 803 the are to possibility for this alarm f107 or f 109 but t dont know the solution about this alarm plz thank you mester
-
16-07-2009, 10:16 PM #27
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
I have probleme in daikin refeer al 803 plz what a wil doing plz mau prof
mu email/ hichamviolon@hotmail.com
-
16-07-2009, 10:46 PM #28
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
yes my prof some times i tchek the eev is good end when i make of in the reffer end make on it work normal end in rang but after 3hour or 2hour the some probleme unite stop al 803 .thenks
-
23-07-2009, 03:16 AM #29
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Last edited by Will; 23-07-2009 at 03:24 AM.
-
26-07-2009, 09:20 AM #30
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
.................................
Last edited by reefermechanic; 27-02-2013 at 08:54 AM.
-
26-07-2009, 09:10 PM #31
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
THANK YOU PROFESSOR AND FOR YOUR HELPEND Gentille
REALLY I NEED YOU FOR ADVICE OF REEFERS PROBLEMS .thank you
IF THAT possibl TO still be contacted my email : troytroy@live.fr
THANKS
-
18-07-2009, 04:32 AM #32
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Thankyou my teacher
for al803 i know that it is acause the 107 or 109 to 10 times.
All fuse are ok
servo motor running eev ok
what a did i make reefer off end on then he travel normal byt after time reefer out of rang end al e107 or e 109
plz help me because i have 3 reefers in terminal morocco
thanks
-
19-07-2009, 03:13 PM #33
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hallo again...
After checking the electronic cards of my container, we got it running. Now there are some simple things i donto know.
On the control board are some switches wich i dont know what they do. I'm sure you can help.
What is the "HCS" switch for...? What does it do?
What does the "TDS" button...?
What is the "TSS"...?
What is "SDS"...?
All these switches are for something. Please explain them to me...
I'm blind here...
-
29-07-2009, 07:53 AM #34
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi All,
I have problem with my laptop are can't connect communication when used for Carrier container unit/launch pad.
Detail model are acer TravelMate 6292.
Cause the port using usb port so i using serial adpter to joint cable communication with my laptop.
Is it cause that adapter so communication become interupt?or any other suggest
Any kind of response will be highly appreciated
Thank you
-
29-07-2009, 08:04 AM #35
-
17-08-2009, 10:53 PM #36
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi guys,I've got a problem with Carrier 69NT40-511-38 controller M-2.The unit is set up-4C but does not stop gaining temperature when it is -4C inside.There is no any alarm.
Please,give advice
Thanks in advance.
-
05-09-2009, 09:45 PM #37
-
08-09-2009, 11:59 PM #38
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi reefermechanic,
I did not wait when the unit stops because of prodact. I am going to try and inform you.
Regards German
-
09-09-2009, 04:45 AM #39
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
sounds like the unit is overshooting setpoint. those units have a suction solenoid and a suction mod valve. sometimes the SSV sticks and sometimes the SMV sticks in the open spots. try and loosen the SSV its the valve on the right hand side if u are facing the unit. pull off the coil and you should hear a "CLICK" sound. if no click then u have either a stuck valve piston or no voltage to the coil. also check the fuses on the controller. if that checks out ok then its the SMV and u have to check the coil resistance 7.8 ohms. try this first and let us know
-
13-09-2009, 08:22 PM #40
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
HI ALL
I HAVE PROBLEME WITH A TIP in termoking -529
(qeust not allowed ) i want to desacteved but i d'ont now wher or what id the solution for this tip
best regard
troytroy@live.FR
-
13-09-2009, 08:27 PM #41
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
HAY ALL
A HAVE PROBLEME WITH (qeust not allowed ) in thermoking i want to desacteved at disply but i d'ont now the solution for desacteved ;
plz help
-
14-09-2009, 07:18 AM #42
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi terminal,
I think you want to clear alarm on TK unit, isn't it???You chek below mationed...
Viewing the Alarm List MenuWith theUNIT ON/OFF switch ON and the LCD
display showing the standard display (setpoint):
1. Press F2 key to directly enter the Alarms
menu. The first alarm code number, alarm
state and alarm description appears in LCD
display.
NOTE: Alarm codes are displayed in
sequential order, not in the order of
occurrence.2. Write down the first alarm code. Then pressF2key to view the next alarm code when
more than one alarm code has been recorded.
3. Repeat step 4 until all alarm codes have been
recorded. To scroll backward to return to a
previous alarm code, press F3 key.
4. To clear all alarm codes from the current
display list and turn off the Alarm LED, all
problems must be corrected and the alarm
code “acknowledged” in the Alarm List menu.
NOTE: To acknowledge an alarm, press F4Alarms Menu level or the LCD Standard Display.
while the alarm code appears on the screen.
The alarm state will change from Active or
Not Active to Acknowledge.
NOTE: If no key is pressed for 30 seconds,
the controller returns to the previous menu
-
17-09-2009, 01:06 AM #43
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi reefermechanic,
I HAVE PROBLEME WITH A NEW CARRIER PRIMLINE .
IF YOU CAN SEND ME MANUEL FOR THIS ONE .
BEST REGARD
TROYTROY@LIVE.FR
-
17-09-2009, 07:58 AM #44
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
..............................
Last edited by reefermechanic; 27-02-2013 at 08:54 AM.
-
21-09-2009, 08:37 AM #45
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Hi all
To Bruisermac
Your suggestion might be true because the unit bekame run properly.
Thanks for ansvering.
-
27-09-2009, 12:10 AM #46
-
27-09-2009, 07:49 AM #47
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
hi all,
I got a problem in Carrier Reefer model 69NT40-511-357. The problem is F1 & F2 (both 5 Amps) keep blowing. I checked the main power and the Control Transformer output, all are normal. Changed the Controller, but still the same. Any idea about the problem's solution?
-
29-09-2009, 01:36 AM #48
-
29-09-2009, 04:33 PM #49
-
30-09-2009, 02:35 AM #50
Re: all reefer container problems/daikin/carrier/thermoking/mitsubishi
Then you have something really messed up in the wiring somewhere.
Something like this; few years back had a 'weird' problem on a TK. Evap fan motor smoked so bad it was feeding high volt back to mother board via motor overload circuit.
You don't know fun till ya find 460V in your control circuit.
Will
Similar Threads
-
Container Reefer Unit for Controlled Atmosphere (CA)
By reeferman in forum New TechnologiesReplies: 9Last Post: 26-08-2011, 09:26 AM -
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
Help cutting open 40ft reefer, we now have problems
By adrian_uk17 in forum IndustrialReplies: 50Last Post: 28-11-2010, 08:11 AM -
Reefer container
By stevec in forum CommercialReplies: 2Last Post: 25-01-2009, 05:30 PM